Electrical Requirements of a typical Guitarmaker's Shop
|
Consult a licensed electrician in your local
area, NEC codes are prevalent across the United States, but local codes
sometimes take precedence over national codes, go figure. Also note:
many local codes require conduit for commercial applications such as a
guitarmaker's workshop. I run Romex or NM sheathed cable only if it is
protected from the workspace in a covered situation. In a new shop it
is great. Remodelling type situations may force you to use EMT or PVC
conduit and fittings.
Typical Workshop 200
Amp Distribution Box, 30 Spaces, 220 Volt
12- 20 Amp 110V. Circuits
for items like this:
6 inch Jointer
4 inch Tabletop Sander
6 inch Floor model 6 x 48 Belt Sander
Router Table with Router
Floor model Grinder
Drill Press, floor model
14 inch Bandsaw
Dehumidifier
Humidifier
And in my shop, 9 light switches
Ceiling drop corded outlets are nice
NEC rates each 110 Volt duplex receptacle at
1.5 amps. Each breaker is rated at 80% of it's face value. So your 20
amp single pole breaker is good for 16 amps or ten receptacles. But
remember, you are in a near commercial environment so you have to look
at power consumption. Anything you plan to have on a circuit, such as
lights, use up power on that circuit, so dropping your bandsaw on there,
might be too much, just add up the amps and if you are over 80 percent
of the breaker's rating, well, it's time for another circuit. And, just
because you don't have a tool in a corner today, plan on it being there
someday, especially if you are wiring a new shop and it's easily run now
where later you may have to run conduit.
4- 20 Amp 220 V. Circuits
for items like this:
18 inch Bandsaw
25 inch Dual Drum Sander
2HP Dust Collector
1HP Buffer
While the most efficient, 220 devices may eat
up box space, each device requires two poles. So here is where box
space may disappear on you when running 220 machines.
40- Amp 220 V. Circuit
Heating Unit with emergency heat strips
30 Amp 220 V. Circuit
Air Conditioning Heat Pump Condensing Unit
Six spaces of the original
30 remain for future expansion
It make sense to plan for future expansion,
beyond even the box you currently use.
I have a basement area under my shop which
eventually will become my spray booth.
It will require power for a compressor, booth
fan, lighting, nitro hot-water bath, etc.
So It'll get a small 12 space subpanel in that
area, the wiring already exists from my subpanel.
For Wire sizes of cables, refer
to the National Electrical Code Book, revised every three years. It is
put out by the NFPA, the National Fire Protection Agency. In many areas
code allows individuals to do their own wiring, when working on their
own property, it's called a Grandfather Clause. In some municipalities
you must hire a licensed electrical contractor, so you have to check,
just to see if it is legal to do your own work.
Of course, you leave yourself
liable by doing the work yourself. Outside receptacles should be GFCI
protected. Sinks in a shop with receptacles within 6 feet are also
required to have GFCI protection, either a GFCI breaker or receptacle.
Please feel free to make other recommendations,
we may add it to this or incorporate it into this article.
Bruce Dickey
|